View Full Version : 230V welder in a 240V plug; will it work...
pipehitter155
06-18-2007, 09:33 AM
well the plug is measure 240V output.....i bought this miller welder:
http://www.weldingmart.com/Qstore/p003461.htm
help me out guys....i got alot of welding to do...thanks ahead of time...
ps.....in case you couldn't tell i don't know shit about electricity....:flipoff2:
OverkillZJ
06-18-2007, 09:37 AM
220-240 is standard, I'd say 230 falls about dead-center!
The instructions should have a normal operating range listed, and 240 should be in there....
Gummi Bear
06-18-2007, 03:00 PM
Assuming nothing weird has happened in the last few months, it should take a NEMA 6-50R receptacle at the wall for it to plug into.
Unless you've got some really wonky voltage at your house or shop, it should operate fine on 220-240V.
u2slow
06-19-2007, 10:59 AM
240V is a 'system' or distribution voltage. 220V & 230V are what equipment are rated for.
That's how its done because some voltage drop is unavoidable, and thus, being designed around the lesser voltage, ensures optimal performance in normal installations.
The 240V you measure at the receptacle is without a load. While laying a heavy bead, you can be sure it dips a little. ;)
EDIT: 120/208V 3Ø is an exception. Equipment that is compatible will be explicitly marked 200V or 208V. While a 220-230V rated machine will most likely run, it will be short on torque, exhibit high current draw, and ultimately - a reduced lifespan.
mrarmyant
06-26-2007, 03:28 PM
Also most (really all) rated equitment is designed to run +-10% of spec due to all the uncontrollable variables. Granted, like said above, it's not supposed to run in that 10% area, but it can.