VFD as phase converter

I Asked about a Rotary Phase converter here Phase converter - Pirate4x4.Com : 4x4 and Off-Road Forum
And some of yall said go with a VFD.

SO, lets talk VFDs.

I have a lathe with a 10HP / 3phase /208-230-460V Motor (World Motors model # T779A ID# T779-B06-6437-M)

The current setup is wired to 3 phase/ 460 power using a Sumitomo AF-500 inverter.

It has become necessary to change the voltage to 208/230 1 Phase.

SO, I need an inverter sized so it can function as a phase converter at the 208/230 voltage.

SO Can I size the VFD for 10HP?

I think I read somewhere that if you are using it as a phase converter you have to de-rate it by HALF, which means I have to get a 20 HP VFD?
I asked a Drive guy about it and he said I cant feed the drive Single phase PERIOD.

What do I need and what size?
Name:  lathe1.JPG
Views: 1077
Size:  143.2 KB

Name:  lathe 2.JPG
Views: 996
Size:  81.1 KB
__________________
There ain't no good in an evil-hearted woman
And I ain't cut out to be no Jesse James
And you don't go writing hot checks down in Mississippi
And there ain't no good chain gang
Grumpy356 is offline   Reply With Quote Quick reply to this message
Old 03-05-2013, 02:49 PM   #2 (permalink)
Registered User
 
Join Date: Apr 2011
Member # 187562
Location: Omaha, NE
Posts: 4
VFD as phase converter

Yea you can. I have a 5hp 3-phase 230v fountain running off 230v single with a VFD running it.

You might try calling a local pump company. They will be able to give you more info on this.
__________________
1999 Chevy S10 ZR2
raven2510 is offline   Reply With Quote Quick reply to this message
Sponsored Links
Old 03-05-2013, 02:57 PM   #3 (permalink)
Rock God
 
Join Date: Jan 2005
Member # 41764
Location: Pleasant Hill, CA
Posts: 2,234
With an RPC you derate the motor making the 3rd leg 1/3rd (i.e. 5hp 3ph motor is only capable of creating a little more than 3hp in 3ph off single phase power).

Using a static phase converter you derate the drive motor 1/3rd as you're only driving it on 2 windings.

With a VFD, look at the manufacturers specs. Some require derating, some don't.

10hp is a lot, 746w per hp so you need basically 34a of 220v power (746*10/220) at peak. IIRC when looking into VFD's most manufacturers only go up to 5hp on single phase input, but 15hp units exist.

In any case, yes, doable with a VFD, just get a big enough one.
__________________
Tow Rig: 2006 Dodge 2500 610CTD/G56/NP271/AAM9.25/AAM11.5
Trail Rig: 1997 K1500 LQ9/4l80e/NP241/D60/14FF and some stuff in between

No one is ever gone if they are always remembered.
JasonPayneMemorial
bggrnchvy is offline   Reply With Quote Quick reply to this message
Old 03-05-2013, 03:03 PM   #4 (permalink)
Hate keeps me warm
 
Grumpy356's Avatar
 
Join Date: Jan 2010
Member # 151139
Location: Brazoria County Texas
Posts: 1,241
Quote:
Originally Posted by raven2510 View Post
Yea you can. I have a 5hp 3-phase 230v fountain running off 230v single with a VFD running it.

You might try calling a local pump company. They will be able to give you more info on this.
What size is the VFD rated?

Is it a 10 HP VFD? Is there anything special about the VFD?
__________________
There ain't no good in an evil-hearted woman
And I ain't cut out to be no Jesse James
And you don't go writing hot checks down in Mississippi
And there ain't no good chain gang
Grumpy356 is offline   Reply With Quote Quick reply to this message
Old 03-05-2013, 03:16 PM   #5 (permalink)
Hate keeps me warm
 
Grumpy356's Avatar
 
Join Date: Jan 2010
Member # 151139
Location: Brazoria County Texas
Posts: 1,241
Quote:
Originally Posted by bggrnchvy View Post
With an RPC you derate the motor making the 3rd leg 1/3rd (i.e. 5hp 3ph motor is only capable of creating a little more than 3hp in 3ph off single phase power).

Using a static phase converter you derate the drive motor 1/3rd as you're only driving it on 2 windings.

With a VFD, look at the manufacturers specs. Some require derating, some don't.

10hp is a lot, 746w per hp so you need basically 34a of 220v power (746*10/220) at peak. IIRC when looking into VFD's most manufacturers only go up to 5hp on single phase input, but 15hp units exist.

In any case, yes, doable with a VFD, just get a big enough one.
SO,

This VFD won't work, because it doesn't show a Single phase input?DURApulse - GS3 Drive Units (230 / 460 VAC SLV) Overview
Am I interpretting his right?
__________________
There ain't no good in an evil-hearted woman
And I ain't cut out to be no Jesse James
And you don't go writing hot checks down in Mississippi
And there ain't no good chain gang
Grumpy356 is offline   Reply With Quote Quick reply to this message
Old 03-05-2013, 03:46 PM   #6 (permalink)
Rock God
 
Join Date: Jan 2005
Member # 41764
Location: Pleasant Hill, CA
Posts: 2,234
Quote:
Originally Posted by Grumpy356 View Post
SO,

This VFD won't work, because it doesn't show a Single phase input?DURApulse - GS3 Drive Units (230 / 460 VAC SLV) Overview
Am I interpretting his right?
Those do have single phase input, but only up to 3hp.

The Hitachi unit I've seen before has a dead link now, hrm. In any case, IIRC, new it was ~$1200. It makes building a 15hp RPC alot more palletable

EDIT: http://www.driveswarehouse.com/p-2125-pc1-100.aspx

There's an option.
__________________
Tow Rig: 2006 Dodge 2500 610CTD/G56/NP271/AAM9.25/AAM11.5
Trail Rig: 1997 K1500 LQ9/4l80e/NP241/D60/14FF and some stuff in between

No one is ever gone if they are always remembered.
JasonPayneMemorial

Last edited by bggrnchvy; 03-05-2013 at 03:47 PM.
bggrnchvy is offline   Reply With Quote Quick reply to this message
Old 03-05-2013, 04:02 PM   #7 (permalink)
Hate keeps me warm
 
Grumpy356's Avatar
 
Join Date: Jan 2010
Member # 151139
Location: Brazoria County Texas
Posts: 1,241
Quote:
Originally Posted by bggrnchvy View Post
Those do have single phase input, but only up to 3hp.

The Hitachi unit I've seen before has a dead link now, hrm. In any case, IIRC, new it was ~$1200. It makes building a 15hp RPC alot more palletable

EDIT: PC1-100

There's an option.
I put together a 5 HP Rotary, and am on the look out for a 15 HP motor, but that still leaves me with a VFD Issue.

Who ever had this lathe, ripped out all the controls and went with the VFD, SO ....


with a rotary converter and a transformer, I could use the VFD that is on it, I guess.

It originally had a super sweet vacuum tube control scheme, but that is LONG gone.
__________________
There ain't no good in an evil-hearted woman
And I ain't cut out to be no Jesse James
And you don't go writing hot checks down in Mississippi
And there ain't no good chain gang
Grumpy356 is offline   Reply With Quote Quick reply to this message
Old 03-05-2013, 05:41 PM   #8 (permalink)
Trainee Shepherd
 
X-Eng's Avatar
 
Join Date: Mar 2013
Member # 265042
Location: Horsham, UK
Posts: 8
I have a Bridgeport Interact rated at 9Hp which I run from a 7.5Hp siemens VFD on single phase without any problem.

I fitted a current meter to the VFD and the only time it gets anywhere near 7.5Hp is if you push the emergency stop button - where I think it puts everything it's got into stopping the spindle!

A 1" deep cut with a 1" cutter in mild steel at about 200mm/min gets up to about 7Hp - but I rarely abuse it like that!

Originally, it would trip the over-current cutout on the VFD when it switched on the spindle. By adjusting the acceleration ramp on the spindle controller - it's fine now but will still reach 4000 rpm in a couple of seconds.

I would just buy the biggest VFD you can afford - but don't worry if it's not quite as high as the motor rating - I doubt you will notice!

Si
X-Eng is offline   Reply With Quote Quick reply to this message
Old 03-05-2013, 08:15 PM   #9 (permalink)
Rock God
 
Join Date: Jan 2005
Member # 41764
Location: Pleasant Hill, CA
Posts: 2,234
Quote:
Originally Posted by Grumpy356 View Post
I put together a 5 HP Rotary, and am on the look out for a 15 HP motor, but that still leaves me with a VFD Issue.

Who ever had this lathe, ripped out all the controls and went with the VFD, SO ....


with a rotary converter and a transformer, I could use the VFD that is on it, I guess.

It originally had a super sweet vacuum tube control scheme, but that is LONG gone.
Ah. So is it still running a gear box for reduction or is it straight drive from that big 10hp motor? 10hp leads me to believe it's straight through but that belt drive leads me the other way.
__________________
Tow Rig: 2006 Dodge 2500 610CTD/G56/NP271/AAM9.25/AAM11.5
Trail Rig: 1997 K1500 LQ9/4l80e/NP241/D60/14FF and some stuff in between

No one is ever gone if they are always remembered.
JasonPayneMemorial
bggrnchvy is offline   Reply With Quote Quick reply to this message
Old 03-05-2013, 10:23 PM   #10 (permalink)
dry-rotter of tires
 
dwilliams35's Avatar
 
Join Date: Dec 2005
Member # 63587
Location: Pattison, TX
Posts: 562
We've got a 20hp pump running on single phase with a VFD, so I know it exists... I also know we paid like five grand for the thing..

On the other hand, in my shop at the house I built a rotary VFD for about thirty bucks with a few freebie contactors and an old motor..


On another note, a VFD really wants to just be running a single motor: you tune it to that particular motor. I just plug whatever I want into the rotary.

VFD's are certainly the class of the league, but they're not the best fit for every shop..

Last edited by dwilliams35; 03-05-2013 at 10:26 PM.
dwilliams35 is offline   Reply With Quote Quick reply to this message
Old 03-06-2013, 11:43 AM   #11 (permalink)
Indefatigable
 
Elvis-n-Texas's Avatar
 
Join Date: Sep 2004
Member # 35904
Posts: 813
Quote:
Originally Posted by Grumpy356 View Post
I Asked about a Rotary Phase converter here Phase converter - Pirate4x4.Com : 4x4 and Off-Road Forum
And some of yall said go with a VFD.

SO, lets talk VFDs.

I have a lathe with a 10HP / 3phase /208-230-460V Motor (World Motors model # T779A ID# T779-B06-6437-M)

The current setup is wired to 3 phase/ 460 power using a Sumitomo AF-500 inverter.

It has become necessary to change the voltage to 208/230 1 Phase.
Would it be too difficult to swap to a 220 Single Phase motor? (looks like its accessible; and belt driven)
__________________
Toyota
86 4Runner, 22RE Fully Restored, Garage Queen
R.I.P, old buddy > 93 PU, 22RE. Gone but not forgotton
Projects
IFS; IRS Buggy Project: STILL! Unfinished, Untested and un-paid for!
Toys
31' Fiver
08 Japanese Market WR-250-X SuperMoto
Tow rig
03 GMC Sierra, Duramax, Allison
Elvis-n-Texas is offline   Reply With Quote Quick reply to this message
Old 03-06-2013, 12:19 PM   #12 (permalink)
Trail Tampon
 
rajincajingt's Avatar
 
Join Date: Feb 2004
Member # 27333
Location: NOLA
Posts: 3,511
Re: VFD as phase converter

All that derate stuff is just a current restriction.

As long as their using diodes on the front end, the single phase will not effect them. After the diodes its just a DC conversion and then the vfd pumps a pulse width modulated DC wave out to your motor.

Just make sure you are powering the control power leads, most of the VFDs build control power from only 2 leads.

We normally use a derate the amperage by half. Toshiba's s11 and s15 VFDs are cheap and will take care of this. The are available up to 20hp.
__________________
83CJ7-LM7 on pane-th400-atlas-HP60 shaved14b-reds-racelines-linked - ORIs

1970 Commando under the knife

Last edited by rajincajingt; 03-07-2013 at 06:56 AM.
rajincajingt is offline   Reply With Quote Quick reply to this message
Old 03-07-2013, 04:19 PM   #13 (permalink)
Registered User
 
Join Date: Apr 2009
Member # 134520
Location: Pierson, MI
Posts: 47
Send a message via AIM to UnusualFabrication Send a message via Yahoo to UnusualFabrication
I got my VFD from this place. These are 230 single phase in 230 three phase out: Teco Westinghouse Phase Converter, AC Adjustable Speed Drive Systems, Distributor
__________________
Chris Allred
UnusualFabrication.com
UnusualFabrication is offline   Reply With Quote Quick reply to this message
Old 03-07-2013, 09:09 PM   #14 (permalink)
Registered User
 
Join Date: Jun 2006
Member # 74528
Posts: 229
While 10HP is about the top end of the common range for single phase anything, it is still in the common range. Your VFD is easily possible but you would be looking at a no-name chinese VFD to stay affordable.

For that unit, looking at the pics, you are going to be way ahead in the end by swapping motors. 10HP single phase motors are available. There is some (small amount) of resale value in your current motor. That is your best bet IMO.
PatJ is offline   Reply With Quote Quick reply to this message
Old 03-08-2013, 03:33 PM   #15 (permalink)
Hate keeps me warm
 
Grumpy356's Avatar
 
Join Date: Jan 2010
Member # 151139
Location: Brazoria County Texas
Posts: 1,241
Quote:
Originally Posted by PatJ View Post
While 10HP is about the top end of the common range for single phase anything, it is still in the common range. Your VFD is easily possible but you would be looking at a no-name chinese VFD to stay affordable.

For that unit, looking at the pics, you are going to be way ahead in the end by swapping motors. 10HP single phase motors are available. There is some (small amount) of resale value in your current motor. That is your best bet IMO.
I just got a Telemecanique VFD, and i hope I am good to go.
__________________
There ain't no good in an evil-hearted woman
And I ain't cut out to be no Jesse James
And you don't go writing hot checks down in Mississippi
And there ain't no good chain gang
Grumpy356 is offline   Reply With Quote Quick reply to this message
Old 03-09-2013, 12:07 AM   #16 (permalink)
Registered User
 
Join Date: Jan 2012
Member # 210036
Posts: 13
I've tricked a few VFD's (allen-bradley 1336 plus) for single to 3 phase by disabling the "incoming line loss" alarm. those drives are getting pretty old now and can be picked up for relatively cheep.
BSInc. is offline   Reply With Quote Quick reply to this message
Old 03-27-2013, 08:41 PM   #17 (permalink)
Hate keeps me warm
 
Grumpy356's Avatar
 
Join Date: Jan 2010
Member # 151139
Location: Brazoria County Texas
Posts: 1,241
Wire sizing.

OK, how do I size the wire.

The motor shows it pulls about 24.6 amps at 230/ 3 phase.

SO, I assume I pull #10 between the VFD and the motor. Sizing the wire for the 3 phase output. OR do I have to size the wire for single phase load?

But what do I pull between the BREAKER and the VFD? I assume 24.6 amps without the power factor.

My algebra is rusty (who are we kidding, it was never good to begin with) what is the formula to back out the power factor?

Thanks.
__________________
There ain't no good in an evil-hearted woman
And I ain't cut out to be no Jesse James
And you don't go writing hot checks down in Mississippi
And there ain't no good chain gang

Last edited by Grumpy356; 03-27-2013 at 08:42 PM.
Grumpy356 is offline   Reply With Quote Quick reply to this message
Old 03-28-2013, 01:15 PM   #18 (permalink)
Registered User
 
Join Date: May 2008
Member # 113934
Posts: 34
Quote:
Originally Posted by Grumpy356 View Post
Wire sizing. OK, how do I size the wire.
NEC Article 310.16. There are derating issues that you're probably not familiar with, same with the different wire types. Romex is typically NM, and THHN and THWN are some of the most common types of wire used. You'll notice the chart says #12 THHN copper is good for 25 amps - this is before deration is accounted for. For your uses, figure #12 is good for 20 amps max, #10 is good for 30 amps, etc.

Quote:
Originally Posted by Grumpy356 View Post
SO, I assume I pull #10 between the VFD and the motor. Sizing the wire for the 3 phase output. OR do I have to size the wire for single phase load?
Size the wire for the single phase load. You can always increase the wire size, you can rarely decrease. If you're unsure, move to the next size larger in wire. Once you've got it hooked up and running, put an amp meter on it and check each phase to see how much you're actually pulling.

Quote:
Originally Posted by Grumpy356 View Post
But what do I pull between the BREAKER and the VFD? I assume 24.6 amps without the power factor.
The VFD should have a nameplate (and if it's new enough, it's own disconnecting means) - check it for the max voltage/amperage the unit will handle. Then remember you're using the equipment for something other than it was originally designed for and increasing wire size won't hurt.
Demonio Irelandes is offline   Reply With Quote Quick reply to this message
Reply

Quick Reply
Message:
Options

Register Now

In order to be able to post messages on the Pirate4x4.Com : 4x4 and Off-Road Forum forums, you must first register.
Please enter your desired user name, your email address and other required details in the form below.
User Name:
Password
Please enter a password for your user account. Note that passwords are case-sensitive.
Password:
Confirm Password:
Email Address
Please enter a valid email address for yourself.

** A VERIFICATION EMAIL IS SENT TO THIS ADDRESS TO COMPLETE REGISTRATION!! **

Email Address:

Log-in

Human Verification

In order to verify that you are a human and not a spam bot, please enter the answer into the following box below based on the instructions contained in the graphic.



Thread Tools
Display Modes

Posting Rules
You may post new threads
You may post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -7. The time now is 03:46 PM.


Powered by vBulletin® Version 3.8.6
Copyright ©2000 - 2014, Jelsoft Enterprises Ltd.
Search Engine Optimization by vBSEO 3.6.0 ©2011, Crawlability, Inc.