Plasma, electrical, home wiring, OH MY!
Well, the UPS guy dropped of my new toy yesterday. A new Hypertherm 1250 80 Amp plasma. Now I need to get my garage wired for it.
I have single phase power at home. I am pretty sure there is no way to get 3 phase power (electrical newbie here, bear with me). Hypertherm says that the peak amp draw at startup on the highest setting for single phase (plasma can do both) is 96 AMP I am pretty sure my box is 200 AMP service. How hard will it be to run a singe 100 AMP circuit in the box? My calculations for about 25-50 feet of wiring is that I need to use 6 guage wire. Who else has run a fat plasma at home with single phase current? Any tips or tricks? Thanks SeanP
__________________
If you are not pissed off, you are not paying attention. |
|
|
|
|
|
#2 (permalink) |
|
Zeus of the Sluice
Join Date: Aug 2001
Member # 6398
Location: CO
Posts: 3,351
|
Um, wow! 96A. What sort of 220 outlets are even rated for that?
6 ga seems a bit small? If you wanna do longer runs that's gonna get costly. All my 220 outlets are 50A for the plasma, IIRC I used #6 THHN, and my longest run was ~70ft so I guess I'm not much help but keep us updated
__________________
"Take 300 people and on average 290 of them just generally suck at life" |
|
|
|
| Sponsored Links |
|
|
#3 (permalink) |
|
Registered User
Join Date: May 2002
Member # 11799
Location: Cleveland, TN
Posts: 1,788
|
I'm only aware of a 50amp outlet. Do you have a pic of your plasma's plug? Or can you tell us, is it the same plug on your 220v welder (if you have one?)
I would check some more around Hypertherm's site for circuit reccommendations. She'll draw that 96amps at startup, then settle down. Your circuit breaker will not trip, all the NEC tables, specifications for overcurrent devices, and specs for conductors, take into account peak current draw. So I would wire a 50 amp circuit with what I will guess is the standard 50amp 3 prong outlet and go for it. Again, I know we've had this discussion before, but I wouldn't consider #6 for anything over 20' or so. Look at it this way. IF it turns out you need some type of bigger outlet, wire it for that first. You could have a 4/0 service entrance cable with a 50 amp plug and overcurrent device (breaker). No problem to OVER spec the conductor, big problems if it's underspecced. The only 6ga conductor I've got left in the house is the 3' run from my subpanel to the welder outlet. My house is wired like a brick shithouse now, I don't know if those were ever wired, but my house is heavy duty. You won't get 3ph power. You probably have 200amp service. I tried to get 400, but they demurred. My freidn who works for the PUD up in WA has 400amp service, lucky bastard. Last edited by rusted; 06-30-2004 at 03:37 PM. |
|
|
|
|
|
#4 (permalink) | |
|
Super Moderator
|
Quote:
I think Rusted covered it pretty well
__________________
>David > 4x4Spot.com >It only hurts the first time you agree with me... >"A little nonsense now and then is cherished by the wisest men." |
|
|
|
|
|
|
#5 (permalink) | |
|
Zeus of the Sluice
Join Date: Aug 2001
Member # 6398
Location: CO
Posts: 3,351
|
Quote:
__________________
"Take 300 people and on average 290 of them just generally suck at life" |
|
|
|
|
|
|
#6 (permalink) | |
|
Registered User
Join Date: May 2002
Member # 11799
Location: Cleveland, TN
Posts: 1,788
|
Quote:
![]() Here's that table. If it's a factory setup, you find what plug it has, then wire your outlet appropriately, and you'll be fine. What I mean is if it's got a 50amp plug, then put in a 50amp outlet CORRECTLY, and that's it.
|
|
|
|
|
|
|
#7 (permalink) |
|
Registered User
Join Date: Oct 2001
Member # 7354
Location: Rocklin, CA
Posts: 2,352
|
thanks for the responses. There is no plug on the unit, just stranded wire to add whatever plug you need. I have an electrician friend coming over this weekend to set it up correctly. Sure it will cost some money, but it's worth it as I set up my business. Custom CNC plasma work, who wants some?
SeanP
__________________
If you are not pissed off, you are not paying attention. |
|
|
|
|
|
#8 (permalink) |
|
Registered User
Join Date: Feb 2000
Member # 39
Location: San Martin, CA
Posts: 3,266
|
Usually anything over 50A should really be hard wired to the circuit breaker.
To run this unit on 230V or 240V input would require a 75A breaker (60A x 1.25) and probably 4 AWG THHN wire for short runs.
__________________
Eric Parts for Sale --> D44 shafts, 6 lug rims, air tank Last edited by Eric; 06-30-2004 at 05:37 PM. |
|
|
|
|
|
#9 (permalink) |
|
Registered User
|
The only receptacles you'll find that are rated for greater than 50A are going to be of the 400Hz variety (for aeronautical use, BIG $$$) You won't find them on a NEMA config chart either. Look in your instruction book, or on the name plate of the plasma cutter. There should be a spot that says Max Fuse Size, or even Recommended Circuit Size. That's what you'll base your circuit and overcurrent protection off of. The 96A load is just an inrush current, the same thing that an arc welder does, it is not a sustained load, and therefore does not tax the circuit, allowing you to derate your wire size.
BTW - #2 is what you'd want for a 96A load (look in the 75* column of T310-16) I'm pretty sure that's not the case. According to this: Hypertherm Owners Manual on the Website It looks like you'll need a 60A circuit at 230V single phase. You can find a 14-60 P cord cap and the coordinating 14-60R receptacle if you choose to have a cord and plug connected setup. NEMA Config chart, showing a receptacle that will work just fine Hope this helps.
__________________
I consider myself a student of the game, it's just too bad I'm in special ed... Last edited by Gummi Bear; 07-02-2004 at 07:13 AM. |
|
|
|
|
|
#10 (permalink) |
|
Registered User
Join Date: Apr 2003
Member # 18989
Location: Utah
Posts: 526
|
The manual should have a recommendation for the size of over current protection.
Usually, something like that would be hard wired to a fused disconnect.
__________________
A flash of lightning illuminated the object, wretch, hideous, filthy daemon. A new species would bless me as its creator. |
|
|
|
|
|
#11 (permalink) |
|
Registered User
Join Date: Feb 2001
Member # 3236
Location: Alberta, Canada
Posts: 3,761
|
My Miller 3080 (80Amp) runs alright off of 50A single phase service at home. In the field it runs off of the 30A 3 phase power from the engine drive. I would give it a go with 50A to start and see if it works for you.
__________________
[QUOTE=Roxywheels]The trolls always out themselves :laughing: :roxy:[/QUOTE] |
|
|
|
|
|
#12 (permalink) | |
|
Registered User
Join Date: Feb 2001
Member # 3236
Location: Alberta, Canada
Posts: 3,761
|
Quote:
Just to illustrate I previously snapped this picture: A 4Pack of Miller Dimension 452's which need ~90A @ 230V 3Phase. Notice the hard wired/fused configuration.
__________________
[QUOTE=Roxywheels]The trolls always out themselves :laughing: :roxy:[/QUOTE] |
|
|
|
|
|
|
#13 (permalink) | |
|
Registered User
Join Date: Jan 2004
Member # 26491
Location: Pine, Co
Posts: 409
|
pimpin my goods
Quote:
I've got a quota to make. |
|
|
|
|
|
|
#15 (permalink) |
|
Cranky Moderator
|
Sean. looks like the general consensus is to hardwire it to a safety disconnect. I concur. Devices that can draw that kind of current don't use receptacles.
It's not a difficult job to add the breaker and do the wiring most of the time. Sounds like your panel is close to where your gona set up the machine. PM me if you want me to try and come by and take a look. I am pretty familiar with this type of wiring.
__________________
85 Toy Xtracab "I DON'T want to understand !!" Click here to donate to the Rubicon Trail Foundation Rubicon Trail Foundation "Wow this is unbelievable" 2013 Cantina for the 'Con supporters! WIN a fully built Toyota pickup at Cantina 2013 Davez Off Road and Trail Gear are supporting Rubicon Trail Foundation We have returning Platinum sponsors for Cantina 2013 with Raceline Wheels and Falken Tires!! |
|
|
|
|
|
#16 (permalink) |
|
Cranky Moderator
|
Sean, I just checked the Hypotherm web page, at most you need a 60amp breaker.
Keep in mind, the Plasma cutter will output more amps that the input required because of how it's designed. Even a 50 amp set up on a receptacle would work. I would call Hypotherm, and verify what they suggest, and you’re golden From the web site: Specifications (where indicated) Input voltages 200 – 600 V, 1- or 3-PH, 50/60 Hz, CSA 230 – 400 V, 3-PH, 50/60 Hz, CE Input current @ 12.0 kW 200/208/ 230/240 (Supply Voltage you need) /480 V, 1-PH: 70/70/ 60/58 (Size breaker you need) /31 A
__________________
85 Toy Xtracab "I DON'T want to understand !!" Click here to donate to the Rubicon Trail Foundation Rubicon Trail Foundation "Wow this is unbelievable" 2013 Cantina for the 'Con supporters! WIN a fully built Toyota pickup at Cantina 2013 Davez Off Road and Trail Gear are supporting Rubicon Trail Foundation We have returning Platinum sponsors for Cantina 2013 with Raceline Wheels and Falken Tires!! Last edited by steveh; 07-01-2004 at 08:35 PM. |
|
|
|
|
|
#17 (permalink) |
|
Registered User
Join Date: Nov 2003
Member # 24467
Location: North of Boston
Posts: 101
|
SeanP, Just to ask a question ... Did you say the power for your shop is coming from the house or did you just comment that the house had a 100 Amp Circuit ? Later,
__________________
NnF Scrambler 1982 / Ford Last edited by NnF; 07-02-2004 at 03:52 AM. |
|
|
|
|
|
#18 (permalink) |
|
Registered User
Join Date: Oct 2001
Member # 7354
Location: Rocklin, CA
Posts: 2,352
|
hey. So I called two different techs at Hypertherm and they each told me that the maximum arc amps at startup is 96 at the highest setting and that I should wire in 100AMP. Now, the unit is rated to sever 1.5" and cut 1.125". I will likely NEVER use that size capacity.
My house has 200 AMP service so I should be able to tap a 100 amp breaker (assuming they even make something that size for residential boxes). Yes, I will put a disconnect near the unit with a slo-blo fuse. Thanks for the info. SeanP
__________________
If you are not pissed off, you are not paying attention. |
|
|
|
|
|
#19 (permalink) | |
|
Registered User
Join Date: Feb 2001
Member # 3236
Location: Alberta, Canada
Posts: 3,761
|
Quote:
__________________
[QUOTE=Roxywheels]The trolls always out themselves :laughing: :roxy:[/QUOTE] |
|
|
|
|
|
|
#20 (permalink) | |
|
Registered User
Join Date: Oct 2001
Member # 7354
Location: Rocklin, CA
Posts: 2,352
|
Cool, thanks for the offer. I have a friend coming over in the AM to help out. Truth be told, I will probably never use the full capacity of this machine to do over 1". I just want the ability to if I get an order for something. I will likely move into an industrial space with 3 phase in a year if all goes well with the business launch. I mean WHEN all goes well. I am totally stoked to start this business
![]() SeanP Quote:
__________________
If you are not pissed off, you are not paying attention. |
|
|
|
|
![]() |