What's the amp capacity on this circuit?

Sorry to start another electrical thread, I didn't want to hijack the other one or ten that are going right niw. I'm looking at picking up a 220v welder, what's the capacity of this circuit, 30a or 60a? I'm not an electrician, and never will be, my Google fu has also failed me today. I lost our house to a fire in 2014, I'd like to not repeat it again.

crawlerman79 is offline   Reply With Quote Quick reply to this message
Old 01-24-2016, 09:59 PM   #2 (permalink)
Registered User
 
nate379's Avatar
 
Join Date: Jun 2003
Member # 20099
Location: AK
Posts: 5,496
Looks like 60 amp dryer and 100 amp A/C. I've never seen those tie bars used before, though though type of breakers are pretty rigged IMO. Should use a larger panel instead.

Least they did use those connectors though, I rented a house that they just used 2 single buss (120v) breakers to feed the kitchen stove, baseboard heat, etc. Couple times I had just one breaker trip and still have 120v feeding. That was the house that with every breaker turned off half the house still had power somehow.

Last edited by nate379; 01-24-2016 at 10:01 PM.
nate379 is offline   Reply With Quote Quick reply to this message
Old 01-24-2016, 10:05 PM   #3 (permalink)
Registered User
 
Join Date: Mar 2003
Member # 18369
Location: Oregon
Posts: 1,002
Sounds like a way to add two 240V circuits to a panel that only has enough room for 1 left.

So what you have is a 240V 30A circuit and a 240V 50A circuit. The metal thing is suposed to pull the other breaker off like the pin does between the 50's.

Why Do They Group Four Circuit Breakers Together? - DoItYourself.com Community Forums

Last edited by Wazzobie; 01-24-2016 at 10:11 PM.
Wazzobie is offline   Reply With Quote Quick reply to this message
Old 01-24-2016, 10:08 PM   #4 (permalink)
The dude abides
 
DEER TICK's Avatar
 
Join Date: May 2008
Member # 114517
Location: Grass Valley
Posts: 1,350
That a quad breaker. 220v 50 amp a/c ,and 220v 30 amp dryer. There is nothing wrong with that breaker.
__________________
Opinions are like assholes.Everybody has one,and most stink!
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.

Last edited by DEER TICK; 01-24-2016 at 10:10 PM.
DEER TICK is offline   Reply With Quote Quick reply to this message
Old 01-24-2016, 10:18 PM   #5 (permalink)
Lurking since 1956
 
papee's Avatar
 
Join Date: Jun 2000
Member # 1041
Location: in a chair
Posts: 10,417
Blog Entries: 7
Send a message via MSN to papee Send a message via Yahoo to papee
Just what it says on the breaker, it doesn't double. They are made that way to split phases. If they were side by side on a double breaker like that both would be on the same phase.
__________________
I made it through the password change of 6/16

95 YJ 4.0 HO
Mildly modded
Yes I still wheel

To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
papee is offline   Reply With Quote Quick reply to this message
Old 01-24-2016, 10:19 PM   #6 (permalink)
Registered User
 
Join Date: May 2007
Member # 90864
Location: Freedom, CA
Posts: 1,363
Quote:
Originally Posted by DEER TICK View Post
That a quad breaker. 220v 50 amp a/c ,and 220v 30 amp dryer. There is nothing wrong with that breaker.
*

* depending what wire is connected to it.
68K20 x Drill is offline   Reply With Quote Quick reply to this message
Old 01-24-2016, 10:26 PM   #7 (permalink)
Pirate4x4 Addict!
 
yozsi's Avatar
 
Join Date: May 2007
Member # 91857
Location: Vallejo, CA
Posts: 6,784
Send a message via AIM to yozsi
oh god, challenger breakers. when alot of current flows through them, they have a weak connection to the bus bar. Take the cover off and make sure there isn't any scorching. That said, i have a challenger panel and its basically obsolete. Breakers are pricey as hell and hard to find locally. I buy em off ebay for cheap. The eaton branded ones are the best.
__________________
92 Nissan Pathfinder- 3 Link SAS, 4 link rear
02 Dodge 2500 QC LB 4x4, CTD daily.

Foreign Car Center
Vallejo, CA
yozsi is offline   Reply With Quote Quick reply to this message
Old 01-24-2016, 10:27 PM   #8 (permalink)
Registered User
 
Join Date: Jul 2009
Member # 139150
Location: Coloma, California
Posts: 6,936
to think of it simply: a 220v appliance whether it's a welder, dryer, whatever uses TWO 110volt circuits to power it (that are on different phases). each of the 110volt phases has to be circuit protected in case it shorts out, and since the machine uses those two phases as a pair, when one phase shorts out and trips the breaker, they want the other phase to shut off also automatically or it could create a dangerous condition. the '30' or '50' on top of each leg of the 110v side of that breaker is the amps at which either leg will trip the breaker.
__________________
[COLOR="red"](input truck specs here to prove level of badass and gain Pirate street cred)[/COLOR]
[COLOR="Red"]<< post picture of badass pirate approved truck doing some epic wheeling[/COLOR]
sjracer is offline   Reply With Quote Quick reply to this message
Old 01-24-2016, 10:28 PM   #9 (permalink)
The dude abides
 
DEER TICK's Avatar
 
Join Date: May 2008
Member # 114517
Location: Grass Valley
Posts: 1,350
Quote:
Originally Posted by 68K20 x Drill View Post
*

* depending what wire is connected to it.
Well without tearing the panel apart,and fawking inspecting the thing,he has a quad breaker.His question is very vague. He's asking about "this curcuit ", when in fact there are 2 curcuits on that breaker.
__________________
Opinions are like assholes.Everybody has one,and most stink!
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
DEER TICK is offline   Reply With Quote Quick reply to this message
Old 01-24-2016, 10:30 PM   #10 (permalink)
Registered User
 
Join Date: Jul 2009
Member # 139150
Location: Coloma, California
Posts: 6,936
Quote:
Originally Posted by DEER TICK View Post
Well without tearing the panel apart,and fawking inspecting the thing,he has a quad breaker.His question is very vague. He's asking about "this curcuit ", when in fact there are 2 curcuits on that breaker.
going to assume that he's talking the 30 amp dryer circuit as it's the only one shown that should be powering a plug.

OP: if that's the case, you may want to pull the cover and see what guage wire is hooked to that breaker. I suspect its only going to be 10 guage, which will be fine for an average small homeowner size mig if your not running the welder on the high settings.
__________________
[COLOR="red"](input truck specs here to prove level of badass and gain Pirate street cred)[/COLOR]
[COLOR="Red"]<< post picture of badass pirate approved truck doing some epic wheeling[/COLOR]

Last edited by sjracer; 01-24-2016 at 10:33 PM.
sjracer is offline   Reply With Quote Quick reply to this message
Old 01-24-2016, 11:27 PM   #11 (permalink)
Registered User
 
Join Date: Nov 2005
Member # 58369
Location: Edmonton
Posts: 9,334
When breakers are locked together like that, the max amp rating comes from a single pole. One corcuit will do 30, the other will do 50.

And yes, those breakers are properly locked together.

Last edited by stevrock; 01-24-2016 at 11:28 PM.
stevrock is offline   Reply With Quote Quick reply to this message
Old 01-24-2016, 11:44 PM   #12 (permalink)
Registered User
 
Join Date: Sep 2010
Member # 168923
Location: Rocklin
Posts: 428
Sorry, my vague question was referring to the 30a portion of the breaker/breakers. I wasn't sure if the amp capacity was limited to one of the breakers or if it doubled. The panel was gone thru after the fire, a few circuits were added to the garage, but I believe the panel is maxed out at this time.

Can a sub panel with a dedicated 60a circuit be ran from this box, or would a new main panel be needed? I'm looking at a 180a 220v mig, everything I'm reading says a 50-60a circuit is needed firvthexweldervto work it's best.
crawlerman79 is offline   Reply With Quote Quick reply to this message
Old 01-25-2016, 12:59 AM   #13 (permalink)
Registered User
 
Join Date: Aug 2015
Member # 601234
Posts: 116
By maxed out to you mean no more spaces for breakers or maxed out on ampacity? Whats the main feed to the breaker box rated at? Depending on what the service to the box is you could wire in a new remote panel with a 60 amp breaker. But being that Square D homelite panels are cheap and your box is obsolete might be easier to put in a whole new box.
Sledhooligan is offline   Reply With Quote Quick reply to this message
Old 01-25-2016, 07:06 AM   #14 (permalink)
Registered User
 
Join Date: Jul 2009
Member # 139150
Location: Coloma, California
Posts: 6,936
a new sub panel would be the way to go.

how big is the main panel? how many amp main breaker does it have? 200 amp would be pretty standard.

the other question is: does your main panel have any more room to put in a 220v breaker? I see that you only have a single slot left, and the quality of your panel was questioned by yozsi earlier.

don't know the legalities of this but you might be able to do this: put in a sub panel right next to that panel, move the dryer circuit over to it and feed that new panel from the space where the dryer circuit was. that new sub panel would have a 30 amp dryer circuit and a 50 amp circuit for the welder. I like to make sure to way overwire to that sub-panel by putting in oversized wire. I don't have my electrical book in front of me, but if it calls for 8 guage then put in 6 guage.

maybe this: swap out a couple of single 20 amp breakers for a twin 20 amp breaker that can feed two circuits and replace that 30/50 breaker with a single 50 amp breaker to feed the A/C and move it up one space. now place in a 60,70 or 80 amp breaker in the bottom slot to feed a sub panel and wire the dryer into that sub panel.

like I also said earlier: that welder will more than likely not draw the full 60 amps ever unless you've got it all the way cranked up. the dryer will not be drawing a full 30 amps (unless it shorts out). if you are running at full welder power, then put a note on the dryer so that no-one uses it until you're done. the likelihood of both being on at the same time isn't very likely, as most welds are only a few minutes in duration. plus, if you pay attention to it, most machines have a duty cycle and you should let it rest. 40% duty cycle means weld for 4 minutes out of every 10 minutes of use.
__________________
[COLOR="red"](input truck specs here to prove level of badass and gain Pirate street cred)[/COLOR]
[COLOR="Red"]<< post picture of badass pirate approved truck doing some epic wheeling[/COLOR]

Last edited by sjracer; 01-25-2016 at 07:10 AM.
sjracer is offline   Reply With Quote Quick reply to this message
Old 01-25-2016, 07:22 AM   #15 (permalink)
Registered User
 
paragon's Avatar
 
Join Date: Dec 2004
Member # 40266
Location: Jackson, MS USA
Posts: 24,072
I've used the twin 20s to make more room.

__________________
[COLOR="Black"].

...
[/COLOR]
[CENTER][FONT="Franklin Gothic Medium"][SIZE="4"]"For God and country, Geronimo, Geronimo, Geronimo"[/SIZE][/FONT][/CENTER]
paragon is offline   Reply With Quote Quick reply to this message
Old 01-25-2016, 07:28 AM   #16 (permalink)
Pirate4x4 Addict!
 
Screwzer2's Avatar
 
Join Date: Nov 2004
Member # 38193
Location: Nevada City, CA under a bridge
Posts: 69,497
Quote:
Originally Posted by sjracer View Post
a new sub panel would be the way to go......etc., etc.
All good points, but what the OP needs to hear is he's likely gonna be running new, larger wire to his welding spigot.

10 ga. wire ain't gonna support a 50A circuit.
__________________
Yesterday is History
Tomorrow is a Mystery
and Today is a Gift
That's why they call it the Present

—Eleanor Rososevelt
Screwzer2 is offline   Reply With Quote Quick reply to this message
Old 01-25-2016, 07:42 AM   #17 (permalink)
Registered User
 
Join Date: Jul 2009
Member # 139150
Location: Coloma, California
Posts: 6,936
Quote:
Originally Posted by Screwzer2 View Post
All good points, but what the OP needs to hear is he's likely gonna be running new, larger wire to his welding spigot.

10 ga. wire ain't gonna support a 50A circuit.
he could do a surface mount sub panel and a welder plug right off of that panel. easy. actually, re thinking this (now that I've had my first cup of coffee), just get a twin 20 amp breaker, move the 30/50 amp breaker up one and now you have enough room for a 70 or 80 amp breaker to either directly feed a 60 amp welder plug or a sub-panel to feed that plug. either way not that difficult.
__________________
[COLOR="red"](input truck specs here to prove level of badass and gain Pirate street cred)[/COLOR]
[COLOR="Red"]<< post picture of badass pirate approved truck doing some epic wheeling[/COLOR]
sjracer is offline   Reply With Quote Quick reply to this message
Old 01-25-2016, 07:45 AM   #18 (permalink)
Pirate4x4 Addict!
 
300sniper's Avatar
 
Join Date: Jan 2004
Member # 26382
Location: Greenwood, Ca
Posts: 23,545
30a dryer, 50a A/C
__________________
It's time to switch to whiskey, we've been drinkin' beer all night.
300sniper is offline   Reply With Quote Quick reply to this message
Old 01-25-2016, 07:54 AM   #19 (permalink)
Registered User
 
Join Date: Feb 2004
Member # 27710
Location: Fall Branch, TN
Posts: 434
Quote:
Originally Posted by Screwzer2 View Post
All good points, but what the OP needs to hear is he's likely gonna be running new, larger wire to his welding spigot.

10 ga. wire ain't gonna support a 50A circuit.
It all depends on the duty cycle of the welding machine. 10 AWG could be plenty for a 50 amp circuit if the duty cycle is relatively low.
thecj3man is offline   Reply With Quote Quick reply to this message
Old 01-25-2016, 08:22 AM   #20 (permalink)
Pirate4x4 Addict!
 
Screwzer2's Avatar
 
Join Date: Nov 2004
Member # 38193
Location: Nevada City, CA under a bridge
Posts: 69,497
Quote:
Originally Posted by sjracer View Post
he could do a surface mount sub panel and a welder plug right off of that panel. easy. actually, re thinking this (now that I've had my first cup of coffee), just get a twin 20 amp breaker, move the 30/50 amp breaker up one and now you have enough room for a 70 or 80 amp breaker to either directly feed a 60 amp welder plug or a sub-panel to feed that plug. either way not that difficult.
True. Not enuf data to know what he's got.

Wouldn't you be more inclined to swap out the panel, rather than tack a sub onto a small obsolete one?
__________________
Yesterday is History
Tomorrow is a Mystery
and Today is a Gift
That's why they call it the Present

—Eleanor Rososevelt
Screwzer2 is offline   Reply With Quote Quick reply to this message
Old 01-25-2016, 08:24 AM   #21 (permalink)
Window Licker
 
bgaidan's Avatar
 
Join Date: Aug 2004
Member # 34948
Location: NC Triangle
Posts: 14,696
Blog Entries: 1
Quote:
Originally Posted by thecj3man View Post
It all depends on the duty cycle of the welding machine. 10 AWG could be plenty for a 50 amp circuit if the duty cycle is relatively low.
This doesn't sound right...
__________________
Quote:
I love Dicks and will continue to shop there.
bgaidan is offline   Reply With Quote Quick reply to this message
Old 01-25-2016, 08:33 AM   #22 (permalink)
Registered User
 
Join Date: Jan 2012
Member # 208624
Location: Edmond, OK
Posts: 3,156
Quote:
Originally Posted by bgaidan View Post
This doesn't sound right...
Because it's not. I believe Peak and Continuous operating amperage of the unit dictate if it can be run on a given circuit, assuming the circuit is designed properly to begin with. I would hope that a 30 amp circuit (according to breaker selected) would have wire sufficient enough to support 30 amp continuous. But I'm no electrician...
__________________
Mountain Havoc Alum - '16
3rd place passenger seat ballast and pointer of rocks

Last edited by 93_Fummins; 01-25-2016 at 08:34 AM.
93_Fummins is offline   Reply With Quote Quick reply to this message
Old 01-25-2016, 08:43 AM   #23 (permalink)
Registered User
 
Join Date: Feb 2004
Member # 27710
Location: Fall Branch, TN
Posts: 434
Quote:
Originally Posted by 93_Fummins View Post
Because it's not. I believe Peak and Continuous operating amperage of the unit dictate if it can be run on a given circuit, assuming the circuit is designed properly to begin with. I would hope that a 30 amp circuit (according to breaker selected) would have wire sufficient enough to support 30 amp continuous. But I'm no electrician...
I am no electrician either, but there is a NEC code that specifically deals with welding machines and how the circuits can be de-rated by duty cycle.

I wont deny that it would be better to wire it up for full potential in case he wants to plug something else into it besides a welding machine. But, if it is hardwired without a plug, it is not required.

Last edited by thecj3man; 01-25-2016 at 08:48 AM.
thecj3man is offline   Reply With Quote Quick reply to this message
Old 01-25-2016, 08:50 AM   #24 (permalink)
Registered User
 
Join Date: Jun 2007
Member # 92618
Posts: 647
30,505,030 amps. Duh
trackerbacker is offline   Reply With Quote Quick reply to this message
Old 01-25-2016, 08:51 AM   #25 (permalink)
Registered User
 
Join Date: Jan 2012
Member # 208624
Location: Edmond, OK
Posts: 3,156
Quote:
Originally Posted by thecj3man View Post
I am no electrician either, but there is a NEC code that specifically deals with welding machines and how the circuits can be de-rated by duty cycle.
I still disagree. Duty cycle, to my knowledge, is machine specific. Regardless of duration at peak amperage the machine can handle, the circuit still needs to be able to handle peak without tripping, and continuous without burning up, whether that's for 10% duty cycle or 100%... But I cannot argue that there are specific wiring codes for welders; I'm just not familiar with them....therefore I digress.

I'd personally prefer a circuit to be able to handle maximum amperage draw of a unit assuming 100% duty cycle at full blast. But, again, no electrician.....
__________________
Mountain Havoc Alum - '16
3rd place passenger seat ballast and pointer of rocks

Last edited by 93_Fummins; 01-25-2016 at 08:55 AM. Reason: Me no sparky
93_Fummins is offline   Reply With Quote Quick reply to this message
Reply

Quick Reply
Message:
Options

Register Now

In order to be able to post messages on the Pirate4x4.Com : 4x4 and Off-Road Forum forums, you must first register.
Please enter your desired user name, your email address and other required details in the form below.
User Name:
Password
Please enter a password for your user account. Note that passwords are case-sensitive.
Password:
Confirm Password:
Email Address
Please enter a valid email address for yourself.

** A VERIFICATION EMAIL IS SENT TO THIS ADDRESS TO COMPLETE REGISTRATION!! **

Email Address:
Insurance
Please select your insurance company (Optional)

Log-in


Thread Tools
Display Modes

Posting Rules
You may post new threads
You may post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -7. The time now is 06:55 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2020, Jelsoft Enterprises Ltd.
Search Engine Optimization by vBSEO 3.6.0 ©2011, Crawlability, Inc.
User Alert System provided by Advanced User Tagging (Pro) - vBulletin Mods & Addons Copyright © 2020 DragonByte Technologies Ltd.
vBulletin Security provided by vBSecurity v2.2.2 (Pro) - vBulletin Mods & Addons Copyright © 2020 DragonByte Technologies Ltd.