Ground fault woes

When I run power somewhere outside for a pump, lights or whatever, I like to install weatherproof receptical so in the future I have a place plug something in. I always use a ground fault receptical. After I install it, I always test it. (Not just the test button, but I plug something in)

So, I bult three story watertower deck a few years ago. Since I have lights and ceiling fans, might as well put plugs on all three levels. Installed and tested. Of course I almost never use them.

Last year I decided to pressure wash the second level roof panels. Plug the electric pressure washer in and nothing. Check it out and the receptical is shot. Not just tripped, it won't reset. So I replaced it and washed the roof.

Last month I wanted to vacuum the water tank on the third level. Plug a small pump in and nothing. Check it out and again the recept is shot. Install a new one and vacuum the tank.

Since I had the vacuum pump right there, I decided to vacuum the water fountain right next to the tower. Of course I plug in to the recept on the bottom floor. You guessed it, no worky.

Ok, I don't know, maybe the tower got struck by lightning.

Today I wanted to run a concrete saw. I recently had a new well dug and put a recept next to it. Plug the saw in and shit. WTF

Am I the only one having this issue? All of these receps were bought from Lowes. I've done a lot of wiring, some fairly serious stuff. But I'm not above admitting a mistake. The problem is what exactly could I be doing wrong? It's not like they are complicated and they all worked when I first put them in.
__________________
Project : Amphibious HEMTT


To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
waterhorse is offline   Reply With Quote Quick reply to this message
Old 09-18-2019, 07:37 PM   #2 (permalink)
E. Spengler
 
Subybaja's Avatar
 
Join Date: Dec 2011
Member # 206384
Location: Spenard, Alaska
Posts: 3,800
I just put in a couple GFCIs last week. The package said "Self-tests regularly, and auto-disables at the end of life for added safety."

Read to me as "shit's gonna break itself."
__________________
We had part of a slinky. But I straightened it.
Subybaja is offline   Reply With Quote Quick reply to this message
Old 09-18-2019, 07:56 PM   #3 (permalink)
Newbie
 
M92pv4u's Avatar
 
Join Date: Dec 2018
Member # 860424
Location: Dos Palos California
Posts: 74
Our company bought a refurbished steam cleaner like eight years ago and it started tripping the gfi plug. So one day it wouldn't stop tripping it and I thought nbd plugged it into a regular receptacle. I climbed under the truck and started cleaning when the heating coil got up to temperature I started getting electrocuted luckily I was able to crawl out from under the truck .moral of the story sometimes it is actually a ground fault no matter how many times the steam cleaner technician checked it out.
__________________
Charlie Daniels of the well rig
M92pv4u is offline   Reply With Quote Quick reply to this message
Old 09-18-2019, 08:01 PM   #4 (permalink)
Registered User
 
Join Date: Jan 2011
Member # 181868
Location: North Florida
Posts: 3,245
Quote:
Originally Posted by M92pv4u View Post
Our company bought a refurbished steam cleaner like eight years ago and it started tripping the gfi plug. So one day it wouldn't stop tripping it and I thought nbd plugged it into a regular receptacle. I climbed under the truck and started cleaning when the heating coil got up to temperature I started getting electrocuted luckily I was able to crawl out from under the truck .moral of the story sometimes it is actually a ground fault no matter how many times the steam cleaner technician checked it out.
This wouldn't bother me. But these are not delivering power period. After replacement the plug in item works with out issue.
__________________
Project : Amphibious HEMTT


To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
waterhorse is offline   Reply With Quote Quick reply to this message
Old 09-18-2019, 08:20 PM   #5 (permalink)
Newbie
 
M92pv4u's Avatar
 
Join Date: Dec 2018
Member # 860424
Location: Dos Palos California
Posts: 74
Ive pulled gfi plugs apart and there were ants in the contacts.
__________________
Charlie Daniels of the well rig
M92pv4u is offline   Reply With Quote Quick reply to this message
Old 09-18-2019, 08:20 PM   #6 (permalink)
Registered User
 
Join Date: Sep 2005
Member # 53528
Location: norcal
Posts: 15,215
are you installing them in a protective box like this?

https://www.amazon.com/gp/product/B00JU532B0

if not you should be
rockyota83 is offline   Reply With Quote Quick reply to this message
Old 09-18-2019, 08:43 PM   #7 (permalink)
Registered User
 
88mitsu's Avatar
 
Join Date: Dec 2008
Member # 125523
Location: DESOTO COUNTY, FL
Posts: 6,930
Quote:
Originally Posted by rockyota83 View Post
are you installing them in a protective box like this?

https://www.amazon.com/gp/product/B00JU532B0

if not you should be
this.

and weather resistant GFCIs?

But, even if you have the bubble covers and an outdoor box, gfcis will still fail often if they are out in the open with no eave or anything to hide under. Smear a bunch of duct seal over the top of the box to try and keep water from running in. Also, install drain holes in the boxes.

GFCIs have circuit boards inside them, if they get wet enough times they stop working. Depending on how it's wired, it might be better to use a GFCI circuit breaker and replace the GFCI outlets with regular weather resistant outlets.

The bLowes here sells Legrand, which IMO is garbage. Leviton FTW.
__________________
START UP THE ROTORS
88mitsu is offline   Reply With Quote Quick reply to this message
Old 09-18-2019, 09:07 PM   #8 (permalink)
Registered User
 
bigun's Avatar
 
Join Date: Apr 2004
Member # 29037
Location: Mountainair NM
Posts: 13,635
If it is on it's own circuit replace it with a GFI breaker, they are more sensitive than the outlet, and are better protection
__________________
“Indeed the safest road to Hell is the gradual one..." C S Lewis
bigun is offline   Reply With Quote Quick reply to this message
Old 09-18-2019, 09:22 PM   #9 (permalink)
Registered User
 
BossBuilt's Avatar
 
Join Date: Sep 2000
Member # 1760
Location: Salem Oregon
Posts: 7,862
Quote:
Originally Posted by bigun View Post
If it is on it's own circuit replace it with a GFI breaker, they are more sensitive than the outlet, and are better protection
This. You don't put GFCI's outside.
BossBuilt is offline   Reply With Quote Quick reply to this message
Old 09-18-2019, 09:28 PM   #10 (permalink)
Registered User
 
Join Date: Sep 2005
Member # 53528
Location: norcal
Posts: 15,215
Quote:
Originally Posted by BossBuilt View Post
This. You don't put GFCI's outside.
yes you do, in protective covers, along with the proper GFCI outlet

Last edited by rockyota83; 09-18-2019 at 09:28 PM.
rockyota83 is offline   Reply With Quote Quick reply to this message
Old 09-18-2019, 09:34 PM   #11 (permalink)
Rednek
 
billybob_81067's Avatar
 
Join Date: Aug 2005
Member # 52387
Location: Rocky Ford, Colorado
Posts: 8,733
Send a message via AIM to billybob_81067 Send a message via MSN to billybob_81067 Send a message via Yahoo to billybob_81067
Those bubble covers are the gayest shit I've ever seen in my life. The few times we've hired an electrician to do work, as soon as the electrical inspector is gone I rip them off and put a normal outlet and a fucking regular outdoor cover on.
__________________
The one, the only, the Dane.
billybob_81067 is online now   Reply With Quote Quick reply to this message
Old 09-18-2019, 09:42 PM   #12 (permalink)
Registered User
 
Join Date: Sep 2005
Member # 53528
Location: norcal
Posts: 15,215
if youre not a retard they work great mine snap shut with an extension cord plugged into them, a gay ass normal outdoor cover doesnt do that so when youre using it its not protected
rockyota83 is offline   Reply With Quote Quick reply to this message
Old 09-18-2019, 10:36 PM   #13 (permalink)
Rednek
 
billybob_81067's Avatar
 
Join Date: Aug 2005
Member # 52387
Location: Rocky Ford, Colorado
Posts: 8,733
Send a message via AIM to billybob_81067 Send a message via MSN to billybob_81067 Send a message via Yahoo to billybob_81067
Quote:
Originally Posted by rockyota83 View Post
if youre not a retard they work great mine snap shut with an extension cord plugged into them, a gay ass normal outdoor cover doesnt do that so when youre using it its not protected
Like I give a fuck if it gets some rain on it... Ohh noes!
__________________
The one, the only, the Dane.
billybob_81067 is online now   Reply With Quote Quick reply to this message
Old 09-18-2019, 10:39 PM   #14 (permalink)
Registered User
 
Join Date: Jan 2011
Member # 181868
Location: North Florida
Posts: 3,245
I'm useing the kind where it's sealed if there are no plugs in them. It's a spring loaded cover with a rubber seal. The wires are in conduit and there's no sign of water when I take them apart. Two of them were under a roof, so no direct water. (Unless some sideways rain. I don't use the outlets but once an awhile. And I'm not useing them while it's raining. The fact is, I didn't use any of them at all except for the initial test.
__________________
Project : Amphibious HEMTT


To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
waterhorse is offline   Reply With Quote Quick reply to this message
Old 09-18-2019, 11:23 PM   #15 (permalink)
Pirate4x4 Addict!
 
vetteboy79's Avatar
 
Join Date: Jun 2004
Member # 31621
Location: Morganville, NJ
Posts: 11,158
Send a message via AIM to vetteboy79
All the outdoor outlets on my porch are standard receptacles. The circuit that runs them goes through a GFCI outlet located in the basement next to the electrical panel, before it heads outside. You only need one GFCI at the beginning of the circuit and it covers the rest of them.

Likewise the ones in my kitchen are the same way...there's a single GFCI at either side of the stove, and then all the ones along the counter are protected by that. Might be something to consider, especially on something like your tower where it's probably all on one breaker anyway.
__________________
The Alternative Rocker - Taurus SHO V6-powered, Explorer-framed, TTB-front, RCV'd, YJ-bodied east coast racer

To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


Flying Pig Racing #512
vetteboy79 is offline   Reply With Quote Quick reply to this message
Old 09-19-2019, 06:33 AM   #16 (permalink)
Wheeler
 
abrzrkr's Avatar
 
Join Date: Apr 2004
Member # 29912
Location: Pennsylvania
Posts: 269
Send a message via AIM to abrzrkr
Quote:
Originally Posted by waterhorse View Post

So, I bult three story watertower deck a few years ago. Since I have lights and ceiling fans, might as well put plugs on all three levels. Installed and tested. Of course I almost never use them.

I am having trouble picturing this thing. You got a build thread?
__________________
If everyone was just like you then what would we need you for?
abrzrkr is offline   Reply With Quote Quick reply to this message
Old 09-19-2019, 07:36 AM   #17 (permalink)
Registered User
 
Join Date: Oct 2005
Member # 54455
Location: NC
Posts: 262
Quote:
Originally Posted by vetteboy79 View Post
You only need one GFCI at the beginning of the circuit and it covers the rest of them.
This. It's got circuit in the name. One protects the entire run. I would swap the breaker in the panel and use water resistant outlets and covers.
__________________
Boats n Does
Deuce 40s is offline   Reply With Quote Quick reply to this message
Old 09-19-2019, 08:21 AM   #18 (permalink)
Registered User
 
Join Date: Oct 2001
Member # 7412
Location: Azle Texas, Aguilar Colorado
Posts: 6,419
double check your neutral..
__________________
m35A2C 4x4 sitting on 49" R2s,suburban 454/465/205 43" ag tires,Durango on tons and 40s
gunracer1 is offline   Reply With Quote Quick reply to this message
Old 09-19-2019, 08:37 AM   #19 (permalink)
Registered User
 
BossBuilt's Avatar
 
Join Date: Sep 2000
Member # 1760
Location: Salem Oregon
Posts: 7,862
Quote:
Originally Posted by rockyota83 View Post
yes you do, in protective covers, along with the proper GFCI outlet
Let me rephrase that. I don't. Bugs don't care about your stinking covers. I've been running my exterior receptacles off indoor GFCI's for 10-15 years now, no issues tests perfect every time. Bugs nest and goo up the receptacles outside. I have a total of 8 all under covers.
BossBuilt is offline   Reply With Quote Quick reply to this message
Old 09-19-2019, 08:44 AM   #20 (permalink)
Registered User
 
Join Date: Jan 2011
Member # 181868
Location: North Florida
Posts: 3,245
Quote:
Originally Posted by M92pv4u View Post
Ive pulled gfi plugs apart and there were ants in the contacts.
So that ruins them or can you wash them out with electric-clean? I do have lots of ants.

Quote:
Originally Posted by vetteboy79 View Post
All the outdoor outlets on my porch are standard receptacles. The circuit that runs them goes through a GFCI outlet located in the basement next to the electrical panel, before it heads outside. You only need one GFCI at the beginning of the circuit and it covers the rest of them.

Likewise the ones in my kitchen are the same way...there's a single GFCI at either side of the stove, and then all the ones along the counter are protected by that. Might be something to consider, especially on something like your tower where it's probably all on one breaker anyway.
I never knew this. Thankyou! I have two dedicated lines to the tower. Can't remember how they are arranged. There's no inside outlet, but I might be able to have just the bottom outlet a GFCI. (It's the most protected)

Quote:
Originally Posted by abrzrkr View Post
I am having trouble picturing this thing. You got a build thread?
No build thread.



Quote:
Originally Posted by gunracer1 View Post
double check your neutral..
Check them for what? If I install a new recept and it works, how could the neutral be bad?
__________________
Project : Amphibious HEMTT


To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
waterhorse is offline   Reply With Quote Quick reply to this message
Old 09-19-2019, 09:18 AM   #21 (permalink)
Registered User
 
Join Date: Oct 2001
Member # 7412
Location: Azle Texas, Aguilar Colorado
Posts: 6,419
My neutral bar was not bonded correctly, I had to add a ground wire. I burnt up two gfi plugs. So I put a regular plug in it’s place. Then I started hearing a buzzing sound. It was a voltage feed back arcing from my disconnect box to my offset adapter. Ran another bare wire to the ground rod and stopped all the weird shit. But what I did was not code approved. But I live out of town so fuckem.
__________________
m35A2C 4x4 sitting on 49" R2s,suburban 454/465/205 43" ag tires,Durango on tons and 40s
gunracer1 is offline   Reply With Quote Quick reply to this message
Old 09-19-2019, 09:44 AM   #22 (permalink)
Registered User
 
Join Date: Jan 2011
Member # 181868
Location: North Florida
Posts: 3,245
Quote:
Originally Posted by gunracer1 View Post
My neutral bar was not bonded correctly, I had to add a ground wire. I burnt up two gfi plugs. So I put a regular plug in it’s place. Then I started hearing a buzzing sound. It was a voltage feed back arcing from my disconnect box to my offset adapter. Ran another bare wire to the ground rod and stopped all the weird shit. But what I did was not code approved. But I live out of town so fuckem.
I'm not an electrician, so I may not know all the terms. I assume the disconnect box is the main panel? When you say neutral bar not bonded, you mean the bar in the main panel where the newtrals go? I don't know what a offset adapter is.

One thing, all my grounds go all the way back to my house. (With the hots and neutrals) Do you think I should have a ground rod at the tower? Would I tie the neutral in there? I was thinking of installing a lightning rod. Would I use this same rod?

This is something I've never quite understood. I've been told to never ground the neutral at the receptical. Both the ground and neutral must go all the way back to the panel seperatly. Obviously, on a 240 V this makes sense, but on a 115 V, I don't get it.
__________________
Project : Amphibious HEMTT


To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
waterhorse is offline   Reply With Quote Quick reply to this message
Old 09-19-2019, 10:54 AM   #23 (permalink)
Registered User
 
fullsize80cherokee's Avatar
 
Join Date: Jun 2003
Member # 20331
Location: CO, USA
Posts: 3,809
I’ve had weird shit happen with Eaton GFCI receptacles that I recently got from Lowes. They wouldn’t reset with the ground hooked up, Problem was solved after I installed a pass and Seymour device.
fullsize80cherokee is offline   Reply With Quote Quick reply to this message
Old 09-19-2019, 11:00 AM   #24 (permalink)
Registered User
 
Join Date: Feb 2006
Member # 67681
Location: Roanoke, VA
Posts: 28,148
Quote:
Originally Posted by waterhorse View Post
So that ruins them or can you wash them out with electric-clean? I do have lots of ants.
Throw some borax in the outlet box - no more insect problems.
__________________

To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.



To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
rugger is offline   Reply With Quote Quick reply to this message
Old 09-19-2019, 11:09 AM   #25 (permalink)
Registered User
 
Join Date: Mar 2006
Member # 68938
Location: eastern Oregon
Posts: 661
Quote:
Originally Posted by 88mitsu View Post
this.

and weather resistant GFCIs?

But, even if you have the bubble covers and an outdoor box, gfcis will still fail often if they are out in the open with no eave or anything to hide under. Smear a bunch of duct seal over the top of the box to try and keep water from running in. Also, install drain holes in the boxes.

GFCIs have circuit boards inside them, if they get wet enough times they stop working. Depending on how it's wired, it might be better to use a GFCI circuit breaker and replace the GFCI outlets with regular weather resistant outlets.

The bLowes here sells Legrand, which IMO is garbage. Leviton FTW.
The weather resistant ones are no different inside, The only difference is stainless screws and a UV resistant plastc body. They are no better at resisting water intrusion than a standard GFCI.

I would be willing to bet it is just cheap GFCIs, I prefer to get them from an actual electrical parts house, I have had great luck with Hubbell.

https://www.ebay.com/i/333282411247?...AaAhdGEALw_wcB
__________________
72 k5 400/350/205 8" lift 4.56s 38" Toyo M/Ts
87 k5 383/400/203/205, 52s 5.13 60/14bff 39.5 rockers
bigbadchev84 is offline   Reply With Quote Quick reply to this message
Reply

Quick Reply
Message:
Options

Register Now

In order to be able to post messages on the Pirate4x4.Com : 4x4 and Off-Road Forum forums, you must first register.
Please enter your desired user name, your email address and other required details in the form below.
User Name:
Password
Please enter a password for your user account. Note that passwords are case-sensitive.
Password:
Confirm Password:
Email Address
Please enter a valid email address for yourself.

** A VERIFICATION EMAIL IS SENT TO THIS ADDRESS TO COMPLETE REGISTRATION!! **

Email Address:
Insurance
Please select your insurance company (Optional)

Log-in


Thread Tools
Display Modes

Posting Rules
You may post new threads
You may post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -7. The time now is 03:07 PM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2020, Jelsoft Enterprises Ltd.
Search Engine Optimization by vBSEO 3.6.0 ©2011, Crawlability, Inc.
User Alert System provided by Advanced User Tagging (Pro) - vBulletin Mods & Addons Copyright © 2020 DragonByte Technologies Ltd.
vBulletin Security provided by vBSecurity v2.2.2 (Pro) - vBulletin Mods & Addons Copyright © 2020 DragonByte Technologies Ltd.