Simple question. Are two 45amp loads on a 10 gauge wire running at 90amps or at 45amps? I know, I know....I'm an electrical dumb a$$....:rolleyes:
 

·
Registered
Joined
·
4,737 Posts
90 amps, which is WAY too much for 10 gauge... or 8 gauge for that matter. (8 gauge = 75 amps continuous)

Either run another wire, or run 6 gauge.
 

·
In GOD we trust. USA
Joined
·
13,089 Posts
Discussion Starter #4

·
Registered
Joined
·
1,232 Posts
NoJoke said:
Yeah but....

I went here and 6 foot calls for 10 to 12 gauge. I'll definately take your word and run 6 gauge....but why the difference in opinion? Just playing safe?

http://www.ancorproducts.com/Technical_information/Wire_calculator.htm
I went there and it spit out 8AWG for 90 amps at 6 feet. Remember, the smaller the gauge (numerically) the less voltage drop. There recomendation for 12 volts is a 3% voltage drop. That's .36 volts for 6 feet. So your load will be seeing 11.64 volts. Not good.
 

·
Registered
Joined
·
519 Posts
Kirchoff’s current law, “The sum of the currents flowing into any point in a circuit equals the sum of the currents flowing out of that point.”

Simplified:

Currents in series add.

In paralell, total current is the sum of all branch circuit currents.
 